Question re generators for those in the know...

Unread post by Walter105 » Wed Mar 20, 2019 9:09 pm

Hi everyone

We've been told that our 500kVA diesel generator that runs our office and production facility is only being used to around 75% of its total generating capacity and that due to it running often at these reduced loads it is actually causing damage to the generator.

Advice is to either pull more power off it to run it up to full capacity or reduce the running times.

This seems odd to me. Why would running it below full capacity for extended periods (between 4 and 12 hours) cause damage to it?
The best place to find a helping hand is at the end of your arm.
OG
Frequent AvComer
Posts: 616
Joined: Tue Jul 03, 2007 1:05 pm
Closest Airfield: FAPS
Location: Potchefstroom
Has liked: 15 times
Been liked: 28 times

Re: Question re generators for those in the know...

Unread post by OG » Wed Mar 20, 2019 9:28 pm

Does not harm the alternator, but it is not good for the engine.
Running at a lower load for extended periods will cause the piston rings to not expand to full seal, and hot gasses can leak past the rings, glazing the sleeves, and depositing excessive carbon into the sump, prematurely contaminating the oil and causing excessive wear. Also, unburnt fuel will cause builup of carbon on the injector nozzles and turbo. Working the engine to full capacity will burn off these deposits.
Be careful, if ridges have built up in the sleeves because of the carbon deposits, running the engine up to max can cause the piston rings to break.
I'd rather be soaring
User avatar
Induna
1k poster
1k poster
Posts: 1127
Joined: Tue Mar 20, 2012 10:01 am
Closest Airfield: FASD
Location: Port Owen - Western Cape
Has liked: 12 times
Been liked: 9 times

Re: Question re generators for those in the know...

Unread post by Induna » Wed Mar 20, 2019 9:29 pm

Hi,

75% load is actually fine. it still gives you spare capacity of 25% to absorb any additional inrush load. Also note that the diesel engine power is de-rated for altitude (assuming you are up on the reef), which means the generator can produce the rated 500kVA but the engine would probably not be able to produce enough power to supply the full rated 500kVA.

A ball park figure of anything between 50-80% rated power will be ok.
Last edited by Induna on Wed Mar 20, 2019 9:31 pm, edited 1 time in total.
Jacques van der Westhuizen
ZU-xxx | VANS RV-8 in the making...
ZS-WSW | Sonerai 2L
User avatar
kwest
Frequent AvComer
Posts: 702
Joined: Thu Apr 03, 2008 6:25 pm
Closest Airfield: FAGC + FALA
Location: Bryanston
Has liked: 7 times
Been liked: 6 times

Re: Question re generators for those in the know...

Unread post by kwest » Wed Mar 20, 2019 9:29 pm

In many respects the same principle as running an aero engine. High loads at constant parameters. Diesel engines particularly like to run under optimum load otherwise they say the cylinders "glaze" or as I understand form a residue in the cylinders that limits optimum performance over time. ?. Also, purely economic , why invest capital at only 75 % return ?
Keith Stannard.

"I've got wild staring eyes. And I've got a strong urge to fly. But I got nowhere to fly to."
User avatar
Ugly Duckling
Fife Thousand feet
Fife Thousand feet
Posts: 5949
Joined: Sat Mar 18, 2006 2:24 pm
Closest Airfield: Brakpan Benoni FABB
Location: Waterkloof
Has liked: 225 times
Been liked: 149 times

Re: Question re generators for those in the know...

Unread post by Ugly Duckling » Wed Mar 20, 2019 9:45 pm

Many gensets have dummy loads which are energised to keep the engine running at optimum rating. They produce huge amounts of heat so proper cooling is required.
Paul Sabatier EAA Ch 575, SSSA, ERGC, ERFC, AeroClub
Long time Cygnet builder
The object is to fly, it does not matter what the object is!
User avatar
Walter105
Too Tousand
Too Tousand
Posts: 2744
Joined: Mon Dec 14, 2009 10:30 pm
Location: Fourways
Has liked: 12 times
Been liked: 23 times

Re: Question re generators for those in the know...

Unread post by Walter105 » Wed Mar 20, 2019 11:28 pm

kwest wrote:
Wed Mar 20, 2019 9:29 pm
Also, purely economic , why invest capital at only 75 % return ?
Sunk cost. Was bought and paid for a number of years ago to run a bigger facility. Restructuring of operations moved it to a smaller facility, and with current loadshedding now the issue and hence the question.

Many thanks to all for the answers.
The best place to find a helping hand is at the end of your arm.
User avatar
Roger
Seven Thousand
Seven Thousand
Posts: 7446
Joined: Fri Oct 17, 2003 3:46 pm
Closest Airfield: FAPE
Location: Port Elizabeth
Has liked: 44 times
Been liked: 146 times

Re: Question re generators for those in the know...

Unread post by Roger » Thu Mar 21, 2019 2:42 pm

Busy installing another 100kva into one of our offices. Was told 60-80% of capacity is the best range to be operated at.
Don’t take things for granted… Tomorrow is not promised.
vanjast
Frequent AvComer
Posts: 766
Joined: Thu Feb 16, 2017 6:08 pm
Closest Airfield: 200
Has liked: 0
Been liked: 16 times

Re: Question re generators for those in the know...

Unread post by vanjast » Thu Mar 21, 2019 9:29 pm

As mentioned, full load is generally not a good idea (unless engine and alternator are rated well above the 'rated' load).

- The engine always requires services intervals anyway - running at light loads and full load would usually require shorter service intervals.

- Although alternators are rated at xyz KVA, most people mistake this for KW - so A 75% load (Calculated) is a good ballpark figure that will keep it within limits.

- A lot of generator alternators I dug into are wired to just within rated limits. This means they will cook sooner than later. Even production of the reputable one's have been farmed off to cheaper production facilities, with 'cheaper' results.

- If a genny is unable to give it's 'rated' power, and the alternator is ok, the engine will need it's internals redone. A clean engine makes a big difference ;)
:D
These users liked the author vanjast for the post:
Induna
User avatar
heisan
Fife Thousand feet
Fife Thousand feet
Posts: 5435
Joined: Mon Sep 19, 2005 3:45 pm
Closest Airfield: Rhino Park
Location: Pretoria
Has liked: 26 times
Been liked: 92 times

Re: Question re generators for those in the know...

Unread post by heisan » Thu Mar 21, 2019 9:55 pm

An interesting document from Caterpillar on the various generator types and how they are rated (I see that it ties to an ISO specification, so these ratings should be quite uniform):

http://s7d2.scene7.com/is/content/Caterpillar/C10282446